Insufficient Ventilation Warning

  • 29 Mar 2024 11:45 AM
    Message # 13336473

    The triggering of an insufficient ventilation warning as described in the Standard 4.5.3 seems to be 16 L/s, but they describe that as a lower limit and there being an upper limit of 40 L/s in some cases. Am I misunderstanding something fundamental? In my first few reads of this I thought it was being described as the ventilation warning would be triggered between 16-40 and couldn't understand why there would be a floor. In reviewing the formula my understanding is that the warning is triggered in cases where the ventilation rate falls below 16 L/s which makes more sense but...

    I can't find anything describing the function of the upper limit or the cases in which it applies.

  • 1 Apr 2024 10:26 AM
    Reply # 13337248 on 13336473

    The idea of ventilation is that there is sufficient fresh air in the building of  5-10 cfm per person. The formula is dependent on floor area as a proxy for occupancy. 

    The lower limit is so that really small houses will still have a minimum amount of fresh air (sufficient for 1 or 2 people) 

    The upper limit is that these will likely not have the same occupant density as smaller homes.   Example:  1000 sq.ft house with 2 bedroom would be designed for 3 people.  A large 10,000 sq ft home would not normally be expected to have 30 people living there.

    Last modified: 2 Apr 2024 11:13 AM | Donald Fast
  • 2 Apr 2024 3:58 PM
    Reply # 13337987 on 13336473

    In case you want a response with the Building Code referenced, see attached image.  The 16 minimum is prescribed by the code and the max 40 lets it fall into 4 or 5 bedroom homes.