Lunos e2 HRV & As-Built blower door test results

  • 18 Feb 2022 12:47 PM
    Message # 12610384
    Deleted user

    Reaching out to the community in regards to As-Built and the Lunos e2 HRV.  The issue is that to reflect normal operating conditions, the Lunos e2 units, having no dampers which can be closed, they are essentially daylighted and have a significant negative effect on the final BDT.

    Any thoughts, experiences and insights?

  • 22 Feb 2022 10:33 AM
    Reply # 12617696 on 12610384

    Hello, we did at least one house. I don't recall any concerns but I would have to check with the field tech that did the door and get back to you.  There are supposed to be air tight units (although no dampers).  If you are interested here is the sales rep:

    Aleks Cvijic
    Sales & Operations

    BE | Built Environment™

    +1 604 220 1610
    www.builtenvironment.ca

  • 23 Feb 2022 2:19 PM
    Reply # 12620585 on 12610384
    Deleted user

    Thanks Angela,

    I have seen a number of Lunos e2 units, but on this particular project, there was 4 within a relatively small building.  Decided to retest out of curiosity, and the difference was over 0.5 ACH.

    Because of the difference, I thought best to reach out for other's experiences.

  • 1 Apr 2022 10:45 AM
    Reply # 12690075 on 12610384

    Are there any through the wall HRV/ERV units that are HVI certified? These units seem really practical for tiny homes so save space and reduce bulkheads but they are not HVI certified making them ineligible for EnergyStar and CHBA NetZero. 